Valence Electrical Training Services is not endorsed, sponsored, or affiliated with any company, trademark, or owner of any trademarks presented in these videos. This material is intended for educational and informational purposes only and any use falls under the Fair Use Doctrine of Section 107 of the Copyright Act.

Click Here if You Use an Omicron Test-Set

Click Here if You Use a Manta Test-Set

Click Here if You Use RTS Software to Perform Your Tests

Click Here if You Want to See More Videos About This Topic


Click “Mark Complete” below after watching the video so you can keep track of your progress.

4 Comments
Collapse Comments
STEVEN (Group Leader) October 22, 2016 at 9:12 pm

Would it be possible to get copies of the plans you used in these training videos for the Omicron? I would like to go through them and see how you made them which is a bit hard to do from watching the videos

Chris Werstiuk (Administrator) October 23, 2016 at 12:10 pm

It doesn’t look like I saved this specific test plan, but you should be able to see something similar in the “State Sequencer” test in this file.

Download the file

Hope it helps.

Hi… How much is the pick up current for 50G element in this video? I can see how you set up the time in state 2 (omicron) but I can’t see how you set up the current on state 2 for not trip. Thanks

Chris Werstiuk (Administrator) January 15, 2018 at 9:38 am

It is the same in all videos = 8.0 A. The No Trip current was 7.5A and the Trip current was 8.0 Amps.