Perform a Ramping Pickup Test via the Human Machine Interface (HMI)

These videos will show you different techniques for ramping pickup tests on a variety of relays that will not require you to change settings.

The first video is unique to SEL relays via a TAR command with a terminal program. This is the method I use most often when testing SEL relays.

 

This video shows you how to test pickup on SEL relays using Quickset software and/or the front panel.

 

This video shows you how to test pickup on GE/Multilin SR relays using software and/or the front panel.

 

This video shows you how to test pickup on GE/Multilin UR relays using software and/or the front panel.

 

This video shows you how to test pickup on Beckwith Electric relays using software and/or the front panel.

 

This video shows you how to test pickup on Siemens relays using software and/or the front panel.

 

This video shows you how to test pickup on ABB relays using software and/or the front panel.

 

Don’t see the relay you test most often here? Add a comment below and we’ll see if we can get it into the office so that we can make a video for it.

 

Click “Mark Complete” below after watching the video so you can keep track of your progress.

8 Comments
Collapse Comments

Hey Chris,

The video description says you will show how to test pickup on a Beckwith relay but then you show how to test automatic ramp pickup with the Manta on a SEL relay. Was there a mistake in the videos description?

Chris Werstiuk (Administrator) May 23, 2017 at 5:38 pm

Thanks for the heads-up.

Should be all fixed now.

Do you have example using Alstom/GE Micom relay or Schneider Micom relay ?
We have a utility that mainly using those type of relay.

Chris Werstiuk (Administrator) January 13, 2021 at 1:43 pm

We don’t have an example of any Micom relays yet.

Are you talking about a modern one, or an old-school k-series?

Do you know a rep in the US I can contact?

What model would be a good feeder relay example?

Joshua Liuga Suiramo March 4, 2021 at 11:01 am

When talking about ” forward fault and reverse fault” :
1. How do the relay determines it is a fault in ” forward or reverse directions?
2. What is the CT connections like for” forward fault and reverse fault”?

Thanks
Joshua

Yudhvir Rajpaulsingh August 3, 2022 at 8:16 pm

Chris,

Is the DIGSI software for Siemens Relays only available for purchase?

Chris Werstiuk (Administrator) August 4, 2022 at 10:33 pm

There is some dispute over that. It reads on the website like it is purchase only, but may people say you can download the software and use a free version.

I’m not sure because the license someone in the 90s gave me still works.

You can check out the comments in https://valence.relaytraining.com/topic/topic-s1-5-01-upload-sel-relay-settings/ and see if they still work.