Meter tests on protected relays connected to open-delta connected PTs can be very confusing. I know I spent a LOT of time trying to figure out the values reported by my first open-delta connected relay during my first simple meter test.  The voltage and current phasors were completely out of whack and didn’t seem to make any sense, especially when I was told to use an old-timey connection like this:

This connection is wrong on many levels, so we spend an entire section on the correct way to simulate open-delta voltages in the upcoming The Relay Testing Handbook: Simplified Motor Protection. Since this post is about the Amp measurements, we’ll keep the description brief here.  Don’t use the connection above! That complexity was required for 20th century test-sets and relays. Use the simple rules for CT/PT connections described in the The Relay Testing Handbook: Principles and Practice and the How to Test Protective Relays Online Seminar:

  • Replace each CT with a test-set current channel.
  • Replace each in-use voltage signal with a voltage channel.

Modern Open-Delta Test-set to Protective Relay Connections You Should Be Using

If you follow these drawings, the voltage connections and injected voltages are much simpler.

The test-set generates the following open-delta connected phasor diagram that looks exactly the same as a wye-connected test-set and protective relay.

 

Unfortunately, that’s not the open-delta connected phasor diagram that the relay will report back to you.

This excerpt from The Relay Testing Handbook: Simplified Motor Testing will explain how an open-delta connected relay measures and reports Amps when connected to open-delta PTs. I hope it saves you the headaches it caused me when I was trying to figure it all out!

“Current Meter Test with Delta Voltages” Excerpt from The Relay Testing Handbook: Simplified Motor Testing

“…what happens to the current angles when you have Delta voltages? Will they be the same as a Wye voltage connection, or should they be different?

Test-Set Channel Prefault

Relay Metering

(GE SR469)

Relay Metering

(SEL-749M)

Magnitude Angle
V1 Voltage 69.28V 0.00° Vab = 4200V @ 0° VAB = 4200V @ 0°
V2 Voltage -120.00° Vbc = 4200V @ 300° VBC = 4200V @ -120°
V3 Voltage 120.00° VCA = 4200V @ 120°
I1 Current 1.000A 0.00° 50A @ ?° 50A @ ?°
I2 Current -120.00° 50A @ ?° 50A @ ?°
I3 Current 120.00° 50A @ ?° 50A @ ?

The answer depends on what the relay uses as a reference. A relay usually uses whatever is connected to Va-Vn as its reference. That’s why the phase angles in the previous “Current with Wye Voltages” section from the Acceptance Testing chapter match. The test-set is connected to the relay as shown in Figure 6-6 where V1 and VN of the test-set are connected to the Relay Va and Vn terminals. The test-set injects 0° from V1 to VN, and the relay uses that as a reference. If V1 and I1 are at 0°, the relay will report the angle as 0° because it is in phase with Va-Vn.

Figure 6-6: Test-Set Connection with Wye PTs

The Delta voltage connections are significantly different as shown in Figure 6-7. Notice that the neutral of the test-set is no longer connected to the neutral of the relay, and that there is a jumper between the Vb and Vn of the relay.

Figure 6-7: Modern Test-Set Connection with Delta PTs

Figure 6-8 displays a phasor drawing showing the differences between Wye and Delta voltages with line currents in-phase with the Wye voltages. Notice the 30° phase shift between the VAN and VAB voltages?

Figure 6-8: Wye/Delta Voltages and Line Current Phasor Diagram

A Delta-connected relay doesn’t see the Wye voltages, so we’ll remove them in Figure 6-9, which is a good representation of what the test-set thinks is happening using Delta voltages and Wye currents.

Figure 6-9: Delta Voltages and Line Current Phasor Diagram

The relay most likely uses whatever is connected to Va-Vn as its reference. If you follow those terminals back in Figure 6-7, you’ll find that they’re connected to V1 and V2 of your test-set, which is the same as VAB on the phasor diagram. Figure 6-10 shows what the relay will think the phasor diagram really is. Did you notice that everything has shifted by -30°?

Figure 6-10: Delta Voltages and Line Current Relay Phasor Diagram

The relay sets the VAB voltage at 0°, and now the current is lagging by 30° as far as the relay metering is concerned, even though the P-N currents and voltages are technically “in-phase”. This can be confusing for relay testers unless they know how the relay determines angles. Always understand how the relay works before you test it.

The expected values in the relay with Delta voltages are shown in the following table.

Test-Set Channel Prefault

Relay Metering

(GE SR469)

Relay Metering

(SEL-749M)

Magnitude Angle
V1 Voltage 69.28V 0.00° Vab = 4200V @ 0° VAB = 4200V @ 0°
V2 Voltage -120.00° Vbc = 4200V @ 300° VBC = 4200V @ -120°
V3 Voltage 120.00° VCA = 4200V @ 120°
I1 Current 1.000A 0.00° 50A @ 30° 50A @ -30°
I2 Current -120.00° 50A @ 150° 50A @ -150°
I3 Current 120.00° 50A @ 270° 50A @ 90°

What happens if the IA current is the reference inside the relay?

The relay phasor diagram reverts back to Figure 6-9 to make the Ian Current 0° and the relay will report the following metering results:

Test-Set Channel Prefault

Relay Metering

(GE SR469)

Relay Metering

(SEL-749M)

Magnitude Angle
A-Phase Voltage 69.28V 0.00° Vab = 4200V @ 330° VAB = 4200V @ 30°
B-Phase Voltage -120.00° Vbc = 4200V @ 90° VBC = 4200V @ -90°
C-Phase Voltage 120.00° VCA = 4200V @ 150°
A-Phase Current 1.000A 0.00° 50A @ 0° 50A @ 0°
B-Phase Current -120.00° 50A @ 120° 50A @ -120°
C-Phase Current 120.00° 50A @ 240° 50A @ 120°

Now that you understand how currents and voltages relate in an Open-Delta connected relay, take another look at the old-timey connection from Figure 6-5 (shown below):

What will the relay see if we add normal current to the test plan as shown below?

Test-Set Channel Prefault

Relay Metering

(GE SR469)

Relay Metering

(SEL-749M)

Magnitude Angle
V1 Voltage 120V 0.00° Vab = 4200V @ 0° VAB = 4200V @ 0°
V2 Voltage 120V 60.00° Vbc = 4200V @ 300° VBC = 4200V @ -120°
V3 Voltage 0V 0.00° VCA = 4200V @ 120°
I1 Current 1.000A 0.00° 50A @ ??° 50A @ ??°
I2 Current -120.00° 50A @ ??° 50A @ ??°
I3 Current 120.00° 50A @ ??° 50A @ ??°

The relay uses whatever is connected to Va-Vn as its reference, so the relay will report the following information:

Test-Set Channel Prefault

Relay Metering

(GE SR469)

Relay Metering

(SEL-749M)

Magnitude Angle
V1 Voltage 120V 0.00° Vab = 4200V @ 0° VAB = 4200V @ 0°
V2 Voltage 120V 60.00° Vbc = 4200V @ 300° VBC = 4200V @ -120°
V3 Voltage 0V 0.00° VCA = 4200V @ 120°
I1 Current 1.000A 0.00° 50A @ 0° 50A @ 0°
I2 Current -120.00° 50A @ 120° 50A @ -120°
I3 Current 120.00° 50A @ 240° 50A @ 120°

Everything looks OK when we look at the numbers, but compare the phasors for our old-timey connection on the left-hand side of Figure 6-11 to the phasor diagram when we correctly simulated the phasors on the right-hand side of Figure 6-11. Do they look the same? They should if we’re doing our jobs correctly.

[one_half_first]

Old Open-Delta Connection[/one_half_first][one_half_last]

Power System Simulation[/one_half_last]

Figure 6-11: Open-Delta Voltage and Line Current Relay Phasor Diagram Comparison

Everything seems to be correct when the Vab voltage numbers are compared to the Ia currents, but the relay is actually measuring a LEADING current.

We can improve this connection by either remembering to lag our currents by 30° for every test, which isn’t practical because we usually modify the current angle when simulating faults. It would be better to alter the voltage angles instead, as shown in Figure 6-12, because the voltage angles in motor protection typically don’t change. Now we will read correct voltage and current angles during our meter test.

Figure 6-12: Old Open-Delta PT Connections with Correct Angles

Test-Set Channel Prefault

Relay Metering

(GE SR469)

Relay Metering

(SEL-749M)

Magnitude Angle
V1 Voltage 120V 30.00° Vab = 4200V @ 0° VAB = 4200V @ 0°
V2 Voltage 120V 90.00° Vbc = 4200V @ 300° VBC = 4200V @ -120°
V3 Voltage 0V 0.00° VCA = 4200V @ 120°
I1 Current 1.000A 0.00° 50A @ 30° 50A @ -30°
I2 Current -120.00° 50A @ 150° 50A @ -150°
I3 Current 120.00° 50A @ 270° 50A @ 90°

The metering results from the modern Delta connection are shown below. Do you see they are identical? You can use either connection to test the relay, but I prefer the modern connection because it requires less thought on my part.

Test-Set Channel Prefault

Relay Metering

(GE SR469)

Relay Metering

(SEL-749M)

Magnitude Angle
V1 Voltage 69.28V 0.00° Vab = 4200V @ 0° VAB = 4200V @ 0°
V2 Voltage -120.00° Vbc = 4200V @ 300° VBC = 4200V @ -120°
V3 Voltage 120.00° VCA = 4200V @ 120°
I1 Current 1.000A 0.00° 50A @ 30° 50A @ -30°
I2 Current -120.00° 50A @ 150° 50A @ -150°
I3 Current 120.00° 50A @ 270° 50A @ 90°

 

This can all get confusing! Especially when you are looking at phase angles. It is always important to understand what your relay uses as a reference if you want to perform a proper meter test.”

Conclusion

I hope this excerpt saved you from the headaches I had trying to figure out the open-delta connected phasor diagrams the first time I tested an open-delta connected relay.

Still confused?  I came across this explanation from a different perspective that might help: https://www.electricalpereview.com/open-delta-transformer-connection/